A 3-phase voltage source inverter is supplied from a 600 V DC source as shown in the figure below. For a star connected resistive load of 20 Ω per phase, the load power for 120° device conduction, in kW, is ____________.

Correct Answer
Solution & Step-by-step Explanation
| Parameter | 180° conduction mode | 120° conduction mode |
|---|---|---|
| Phase voltage (Vph) | ||
| Line voltage (VL) | ||
| RMS load current (Ior) | ||
| RMS thyristor current (ITr) |
Given that, V = 600 V
R = 20 Ω/ph
RMS value of phase voltage (Vₚₕ) = = 0.4082 V
Vph = 0.4082 × 600
Vph = 244.92 V
Load power