A 5 kVA, 50 V/100 V, single-phase transformer has a secondary terminal voltage of 95 V when loaded. The regulation of the transformer is
- A4.5%
- B9%
- C5%
- D1%
Solution & Step-by-step Explanation
Transformer voltage regulation measures how well the transformer maintains its secondary voltage under varying load conditions. Specifically, it quantifies the voltage drop from the no-load condition to the full-load condition, expressed as a percentage of the full-load voltage.
Calculating Transformer Voltage Regulation
The formula for calculating voltage regulation (VR) is:
Where:
- is the no-load secondary terminal voltage.
- is the full-load secondary terminal voltage.
Analyzing the Given Transformer Data
From the question, we have the following information:
- Transformer Rating: 5 kVA
- Primary Voltage: 50 V
- Secondary Voltage (No Load, ): 100 V
- Secondary Terminal Voltage (Loaded, ): 95 V
Step-by-Step Voltage Regulation Calculation
1. Identify the no-load secondary voltage (). In this case, it's the rated secondary voltage, which is 100 V.
2. Identify the full-load secondary voltage (). This is the voltage when the transformer is loaded, given as 95 V.
3. Substitute these values into the voltage regulation formula:
Comparing Calculation with Options
The calculated voltage regulation is approximately 5.26%. Let's compare this with the given options:
- 4.5%
- 9%
- 5%
- 1%
The calculated value of 5.26% is closest to the option 5%. Therefore, the regulation of the transformer is approximately 5% under the specified load condition.