A three-phase cylindrical rotor synchronous generator has a synchronous reactance Xₛ and a negligible armature resistance. The magnitude of per phase terminal voltage is V and the magnitude of per phase induced emf is E. Considering the following two statements, P and Q,
P: For any three-phase balanced leading load connected across the terminals of this synchronous generator, V is always more than E
Q: For any three-phase balanced lagging load connected across the terminals of this synchronous generator, V is always less than E
Which of the following options is correct?
- AP is false and Q is true
- BP is true and Q is false
- CP is false and Q is false
- DP is true and Q is true
Solution & Step-by-step Explanation
Understanding the Synchronous Generator Phasor Equation
For a synchronous generator with negligible armature resistance, the relationship between the induced EMF (), terminal voltage (), armature current (), and synchronous reactance () is given by the phasor equation:
Here:
- is the internally generated voltage (induced EMF) per phase.
- is the terminal voltage per phase.
- is the armature current per phase.
- is the synchronous reactance per phase.
- ' ' represents a leading phase shift.
The term ' ' represents the voltage drop across the synchronous reactance.
Analyzing Load Conditions
The relationship between and depends significantly on the power factor of the load, which determines whether the armature current leads or lags the terminal voltage .
| Condition | Current () relative to | Effect of ' ' term | Magnitude Relationship ( vs ) |
|---|---|---|---|
| Lagging Load (Inductive) | lags by angle () | leads by . The component of ' ' along is . This component is positive and adds to . | |
| Leading Load (Capacitive) | leads by angle () | leads by . The component of ' ' along is . This component is negative and subtracts from . | can be less than, equal to, or greater than , depending on load conditions. |
Statement P: For any three-phase balanced leading load connected across the terminals of this synchronous generator, is always more than .
Let's analyze this using the phasor equation. For a leading load, leads . Let and , where is positive.
The equation is . Substituting the phasors:
The magnitude squared of is:
Wait, let's re-calculate the magnitude squared using where , , is real axis, . .
Since are positive magnitudes and for a leading load, . The term is negative. This means is less than . It is possible for to be less than if the term is sufficiently large compared to . For instance, with a highly capacitive load (large , approaching ), can become significantly smaller than . Therefore, the statement " is always more than " is false.
Evaluating Statement Q
Statement Q: For any three-phase balanced lagging load connected across the terminals of this synchronous generator, is always less than .
For a lagging load, lags . Let and , where is positive.
The equation is . Substituting the phasors:
The magnitude squared of is:
Since , , , and (for ) are all positive quantities, the term is always positive.
Therefore, is strictly greater than , which certainly means . Consequently, .
So, the statement " is always less than " is true.
Conclusion
Based on the analysis:
- Statement P is false.
- Statement Q is true.
This corresponds to option 1.