Two wattmeter method is used for measurement of power in a balanced three-phase load supplied from a balanced three-phase system. If one of the wattmeters reads half of the other (both positive), then the power factor of the load is
- A0.532
- B0.632
- C0.707
- D0.866
Solution & Step-by-step Explanation
Understanding the Two-Wattmeter Method in 3-Phase Power Measurement
The two-wattmeter method is a common technique used to measure the total power consumed by a balanced three-phase load connected to a balanced three-phase supply. This method involves using two wattmeters connected in a specific way to capture the power flow in the system.
Wattmeter Readings in a Balanced 3-Phase System
For a balanced three-phase system, the readings of the two wattmeters ( and ) can be expressed in terms of the line voltage (), line current (), and the phase angle difference () between the phase voltage and the phase current for the load. The formulas are:
-
-
The total power () consumed by the load is the sum of the readings of the two wattmeters:
Analyzing the Given Condition
The problem states that one of the wattmeters reads half of the other, and both readings are positive. Let's assume is the larger reading and is the smaller reading. Therefore, we have:
Substituting the formulas for and into this condition, we get:
We can cancel out from both sides, as they are non-zero for a power system:
Calculating the Power Factor
Now, we expand the cosine terms using trigonometric identities:
Applying these identities with and :
We know that and . Substituting these values:
Multiply both sides by 2:
Rearrange the terms to group and :
Combine like terms:
Now, we find the ratio of to (which is ):
The angle for which is .
The power factor (PF) is given by :
Calculating the value:
Since both wattmeter readings are positive, the power factor angle must be between and for the larger reading and between and for the smaller reading. Our calculated angle of satisfies this condition, leading to positive readings for both wattmeters.
The two-wattmeter method is a common technique used to measure the total power consumed by a balanced three-phase load connected to a balanced three-phase supply. This method involves using two wattmeters connected in a specific way to capture the power flow in the system.
Wattmeter Readings in a Balanced 3-Phase System
For a balanced three-phase system, the readings of the two wattmeters ( and ) can be expressed in terms of the line voltage (), line current (), and the phase angle difference () between the phase voltage and the phase current for the load. The formulas are:
-
-
The total power () consumed by the load is the sum of the readings of the two wattmeters:
Analyzing the Given Condition
The problem states that one of the wattmeters reads half of the other, and both readings are positive. Let's assume is the larger reading and is the smaller reading. Therefore, we have:
Substituting the formulas for and into this condition, we get:
We can cancel out from both sides, as they are non-zero for a power system:
Calculating the Power Factor
Now, we expand the cosine terms using trigonometric identities:
Applying these identities with and :
We know that and . Substituting these values:
Multiply both sides by 2:
Rearrange the terms to group and :
Combine like terms:
Now, we find the ratio of to (which is ):
The angle for which is .
The power factor (PF) is given by :
Calculating the value:
Since both wattmeter readings are positive, the power factor angle must be between and for the larger reading and between and for the smaller reading. Our calculated angle of satisfies this condition, leading to positive readings for both wattmeters.